CEILING CONCEALED AC DUCTING
4 posters
CEILING CONCEALED AC DUCTING
Anyone who had experience installing this type of unit? The problem is the ducting, I have to cross a beam, I'd like to know what's the minimum diameter of pipe sleeve i could use (I had no other options)or rectangular opening dimensions. I have a clear 500mm under slab>proposed ceiling clear opening,beam height is @500mm.Thanks in advance.
yaug_03- CGP Guru
- Number of posts : 1911
Age : 41
Location : Cainta,Rizal
Registration date : 05/07/2009
Re: CEILING CONCEALED AC DUCTING
.
Seek the advice of the structural engineer. We experienced the same but the SE is only allowing 150 mm dia pipe sleeve max. , beam depth is 600mm.
.
Seek the advice of the structural engineer. We experienced the same but the SE is only allowing 150 mm dia pipe sleeve max. , beam depth is 600mm.
.
oRangE.n.GreeN- CGP Guru
- Number of posts : 1078
Age : 97
Location : Sultanate of Oman
Registration date : 08/11/2008
Re: CEILING CONCEALED AC DUCTING
Thanks dude!oRangE.n.GreeN wrote:.
Seek the advice of the structural engineer. We experienced the same but the SE is only allowing 150 mm dia pipe sleeve max. , beam depth is 600mm.
.
yaug_03- CGP Guru
- Number of posts : 1911
Age : 41
Location : Cainta,Rizal
Registration date : 05/07/2009
Re: CEILING CONCEALED AC DUCTING
how about split type acu na lang? sa isang project namin hindi pinayagan mag sleeve ng 6" dia.
whey09- CGP Guru
- Number of posts : 1869
Age : 42
Location : Quezon City/ Pampanga
Registration date : 02/10/2008
Re: CEILING CONCEALED AC DUCTING
Last resort ko yan pag wala na talaga.Tignan ko muna kung payagan ng structural engineer yung 6"dia.whey09 wrote:how about split type acu na lang? sa isang project namin hindi pinayagan mag sleeve ng 6" dia.
yaug_03- CGP Guru
- Number of posts : 1911
Age : 41
Location : Cainta,Rizal
Registration date : 05/07/2009
Re: CEILING CONCEALED AC DUCTING
Gaano kalaki ba ito bro? usually kasi ang main duct nasa isang side tapos may mga branches lang papunta sa other side.
Hindi advisable ang sleeves dito, para lang sa electrical yun at maliliit lang.
You should do everything below the bottom of the beam. at least 800mm ka dyan sa main duct.
isang option is split type na upright 3 tonner. other option is drop ceiling sa mismong duct lang, the rest ay exposed.
Hindi advisable ang sleeves dito, para lang sa electrical yun at maliliit lang.
You should do everything below the bottom of the beam. at least 800mm ka dyan sa main duct.
isang option is split type na upright 3 tonner. other option is drop ceiling sa mismong duct lang, the rest ay exposed.
Re: CEILING CONCEALED AC DUCTING
.
Can you do a quick sketch of the space bro. Kung maliit lang naman ang room, ilagay mo lang yung return sa kabila but make sure you leave at least 150mm clear space along the beam. Naka-cast na ba? Baka pwedeng horizontal beam or upstand beam.
.
Can you do a quick sketch of the space bro. Kung maliit lang naman ang room, ilagay mo lang yung return sa kabila but make sure you leave at least 150mm clear space along the beam. Naka-cast na ba? Baka pwedeng horizontal beam or upstand beam.
.
oRangE.n.GreeN- CGP Guru
- Number of posts : 1078
Age : 97
Location : Sultanate of Oman
Registration date : 08/11/2008
Re: CEILING CONCEALED AC DUCTING
whey09 wrote:how about split type acu na lang? sa isang project namin hindi pinayagan mag sleeve ng 6" dia.
Depende sa location, number at depth ng beam.
Hindi maganda pero you may also want to consider casette type ACU.
.
oRangE.n.GreeN- CGP Guru
- Number of posts : 1078
Age : 97
Location : Sultanate of Oman
Registration date : 08/11/2008
Similar topics
» Approved Client's pantry
» Madumi ang Ceiling
» dark ceiling
» PLASTERING OF CONCRETE CEILING
» ceiling design site
» Madumi ang Ceiling
» dark ceiling
» PLASTERING OF CONCRETE CEILING
» ceiling design site
Permissions in this forum:
You cannot reply to topics in this forum